地库排烟和排风是否合用一台单速风机?

地库内排烟量和排风量经计算相差不大,如果按双速风机选择,排风用低速,排烟高速排烟量会很大,是否可以直接采用单速风机?,双速风机排风和排烟采用不同的控制模块,那单速风机系统控制又要如何要求?

SDXDS | 2025-03-16 11:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

小唐12321 2025-03-17 08:29 00 [回复]举报

要满足排烟量就可以啊

EHS专家-DL 2025-03-17 11:20 00 [回复]举报

一般认为地库排烟和排风采用单速风机是有以下条件

排烟量与排风量差额比例要求‌:当排烟量与排风量的差额占排烟量的比例<30%时,可采用单速风机,按两者最大值选型‌。若排烟量与排风量相差不大(例如按换气次数计算排风量接近排烟量),单速风机可满足两种工况需求‌。

单速风机系统控制要求

1、排烟优先控制:火灾时强制切断排风模式,切换至排烟模式,并联动火灾报警系统‌。

2、‌独立控制模块:排烟功能需独立于排风系统控制模块,避免非消防状态误触排烟模式‌。

3、消防联动补风:排烟启动时需联动补风系统,补风量不低于排烟量的50%‌。


注意事项

1、单速风机风管需同时满足排烟风速(≤20m/s)和排风换气效率(5~6次/h)要求‌。

2、补风量需同时满足平时排风量的80%~90%和消防排烟量的50%,取两者较大值选型补风机‌。

潘天坤 2025-03-17 13:29 00 [回复]举报

可以考虑单速风机,按照排烟或者排烟计算最大值取即可

汽车库排烟和排风合用系统的时候,一般风口也是共用,保证风量符合要求也可以使用单速风机